I return to the problem of scaling & ranging as no satisfactory reply was forthcoming earlier, by now rephrasing the query.
In this application, I would like to know how an Arithmetic block in FFb can be configured as a divider for a compression ratio calculation for a surge line application, with AI1 (discharge pressure) = 0-1000 psig and AI2 (suction pressure)=500 psig. The ratio output is 1.0-2.5 on 0-100% scales.
As per conventional “normalizing” equation method, a fundamental equation of the form
OUTs = [Km * (Kx * X + Bx) / (Kz * Z + Bz)] + Bo may be simplified further as discharge pressure X and suction pressure Z operate over their 100% span can lead to Kx = 1 and Kz = 1. So the equation becomes: OUTs = [Km * (X + Bx) / (Z + Bz)] + Bo
Conventional methods lead to gain & bias values: Km = 1.33, Bx = 0.0147, Bz = 0.0294 and Bo = - 0.67.
How would I go about in FFb systems in configuring the system? How is scaling, ranging, normalization & computation effected – Is it in EU or % that the calculation performed and at what point does any unit conversion need to take place. Do I need auxiliary blocks?"
In this application, I would like to know how an Arithmetic block in FFb can be configured as a divider for a compression ratio calculation for a surge line application, with AI1 (discharge pressure) = 0-1000 psig and AI2 (suction pressure)=500 psig. The ratio output is 1.0-2.5 on 0-100% scales.
As per conventional “normalizing” equation method, a fundamental equation of the form
OUTs = [Km * (Kx * X + Bx) / (Kz * Z + Bz)] + Bo may be simplified further as discharge pressure X and suction pressure Z operate over their 100% span can lead to Kx = 1 and Kz = 1. So the equation becomes: OUTs = [Km * (X + Bx) / (Z + Bz)] + Bo
Conventional methods lead to gain & bias values: Km = 1.33, Bx = 0.0147, Bz = 0.0294 and Bo = - 0.67.
How would I go about in FFb systems in configuring the system? How is scaling, ranging, normalization & computation effected – Is it in EU or % that the calculation performed and at what point does any unit conversion need to take place. Do I need auxiliary blocks?"