Beamex MC6

I am investigating a plant trip caused by the connection of a Beamex MC6 to a Yokogawa Foundation Field network. The MC6 was connected to a spare port in the field. The MC6 was set so it would not supply a power source. The MC6 draws approximately 20mA.

The plant tripped when the MC6 was set to scan the network. For the initial scan duration of 2-3minutes the connected Foundation Field Bus devices went into an I/O Alarm State. Once the scan completed the I/O alarm went away and the network resumed normal operation. Without disturbing the physical connection, the network was scanned again. The second scan did not cause the I/O alarm and took approximately 30 seconds. When the MC6 was physically disconnected from the network, reconnected and then set to scan the same alarm and 2-3minute scan time occurred.

No settings were changed on the Beamex MC6, it was used as per the manual.
 

Bookmarks

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is Off
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Site Testing and calibration of FF devices mohantg Fieldbus User's Network [FUN] 20 August 17th, 2009 10:09 PM


All times are GMT -5. The time now is 12:16 PM.


Powered by vBulletin® Version 3.8.9
Copyright ©2000 - 2017, vBulletin Solutions, Inc.
(c) 2011-2015 by FieldComm Group. All rights reserved.